Two cutler –hammer advantage starters are doing the same thing:& p* l t$ ~! N% _9 z/ X
After start 2-3 times, they will quit working, if you toggle the start and stop buttons on DCS screen , you will get another 2-3 running before they quit working again.
8 N* @! `, x5 g/ YIt is a cycle.
4 ?4 M: D1 S+ O, c* P5 {0 \! t! y' y/ u- Q. H
We isolate the network control and use the local start and stop only, the problem remains.
: j1 J9 F; u, lSwap one of the defective buckets with a good one, the new bucket works fine.+ y+ e2 ?! ?, K" n) B, k8 ^! c
The problem should be inside the bucket.
( o( W1 O3 n9 x* P4 N
" m$ q" D- U+ ~" fWhen the problem happened, we observed that the contactor has a pulling action but will not seal.
+ B4 ^9 w6 a# M# `+ g" }6 `Use a terminating screw divers to push in the contactor, it will not seal either.
~0 ~9 L5 r e! j! k, _Confirm with TECH support this should be a problem with the control circuit board inside the advantage starter, we bought two new control circuit boards and replaced the old ones, the problem is still the same.. k7 @( B6 S9 K2 R
% t: P5 f% O$ F) WThe next thing we can think of is the coil, we took the coil out to have a close look./ R. m8 Y" R( j0 z
They have a fork to pinch inside the two leads to make connection, it is not a good design at all. We soldered the connection and tried again.
( E2 Q% j! o' M8 F6 o, Y It is getting better this time, we have 7-8 times of running before it quit working.
: }3 a' I2 ~$ S) p+ r$ f Z h1 U
; }0 a4 s+ O8 N. y I$ E0 T. B' HThe coil should be the problem, we ordered two of them. But it will take 5-6 weeks for us to get them. 0 u0 M0 c; l& ^$ \
$ G9 n2 {5 N- i0 k% s0 Y
Do you guys have any input on this issue? |
|