Two  cutler –hammer advantage  starters are  doing the same thing:
& o2 d* Y2 _" K. Q# x3 Q/ g4 p" H After start 2-3 times, they will quit working, if you toggle the  start and stop buttons on DCS screen  , you will get another 2-3 running before they quit working again.
( y  a! ~% ?7 qIt is a cycle.
6 x# J" z; d! u
0 k5 I' ^6 v0 e( n! R* J7 ~3 [5 H. zWe isolate the network control and use the local start and stop only, the problem remains.
* W/ U5 |/ Q; a. D# N, O: BSwap one of the defective buckets with a good one, the new bucket works fine.8 S& b8 @% i0 k5 U: J
The problem should be inside the bucket.
, Y8 m, m3 w9 S; D( _% Y
9 e5 w; Z% i8 X" UWhen the problem happened, we observed that  the contactor has a pulling action but will not seal." M+ D: |9 I; G, r7 n- {  _% C
Use a terminating screw divers to push in the contactor, it will not seal either.
/ @; |# K# G. P7 _7 oConfirm with TECH support this should be a problem with the control circuit board inside the advantage starter, we  bought two new control circuit boards and replaced the old ones, the problem is still the same./ `& ^" t% T) c1 C
2 r# M% _: [5 V5 N" o+ F
The next thing we can think of  is the coil, we took the coil out to have a close look.
, @1 `& V9 X; \; B5 r* j& wThey  have a fork to pinch inside the two leads to make connection, it is not a good design at all. We soldered  the connection and tried again.
8 x8 V. I1 B0 c& s$ n' ? It is getting better  this time, we have 7-8 times of running before it quit working.
3 V. _  l* I/ I$ e& g* n* i0 }  C/ w" Q* J5 |" J
The coil should be the problem, we ordered two of them. But it will take 5-6 weeks for us to get them. * r% w- m" K) C  o  x* ^
- q( b6 b9 W' \1 M+ u# {  \
Do you guys have any input on this issue?
大型搬家
鲜花(1) 鸡蛋(0)
发表于 2010-3-26 17:07 | 显示全部楼层
有时候主接触点太脏,也会造成启动器无法正常工作
鲜花(0) 鸡蛋(0)
发表于 2010-3-26 17:37 | 显示全部楼层
本帖最后由 贾电工 于 2010-3-26 18:38 编辑 : `! U1 S+ W" ~& k7 R9 w

: |% G6 d; t6 G& D% q( k中国人在这里最好说中国话!说英语或想学英语请人到洋人论坛!
鲜花(7) 鸡蛋(0)
发表于 2010-3-26 17:42 | 显示全部楼层
老杨团队 追求完美
Don't know cutler –hammer advantage  starters very well, but had been worked on AB switch gears for a little while, which has two different coils, one to pull the vacum bottles up which employs larger current, another one uses less current to hold the connection---if the second coil fails, it won't be able to seal the connection.3 m' w9 |2 r" g" @' e. J
Since your cutler -hammer works couple times,  I guess 侠客行 is right, or the sealing connection is just worn out.
理袁律师事务所
鲜花(0) 鸡蛋(0)
 楼主| 发表于 2010-3-26 17:55 | 显示全部楼层
2# 侠客行 ; `+ Y/ L& y. X+ h! n
也想到这一点,不过这是新装的设备。
- m2 {' s* f9 P) c( t检查过触点没问题。