6 _! G- z5 j; m7 |% sWe all know that if you want to change the rotation of a three  phase AC motor.
2 k# d1 x% F) T  Z) V8 EJust swap any of the two phase leads." y7 N0 y) }6 a& q3 @7 z/ Q: I
But for VFD application you need to do the swap after the inverter.
  j( Y8 n+ g3 `If you swap the leads before the inverter, it will not work.
鲜花(0) 鸡蛋(0)
发表于 2010-4-14 18:18 | 显示全部楼层
go go go
理袁律师事务所
鲜花(0) 鸡蛋(0)
发表于 2010-4-19 14:38 | 显示全部楼层
Yes, Good point.5 D! P8 z2 `& L1 o

0 _$ [9 a/ k: G$ @! L4 v4 M% WAs the principal of the VFD works, bascially from AC to DC, then DC to AC. 2 g4 d# E/ i& Z) _/ ]& j
& A& h3 `, E' Q
The phase rotation of the output of the VFD connecting to the motor is based on the sequence "open" or "close" controlled by the inverter pre-set inside; any changes to the phase rotation of the feeder will not affect the DC rotation, as DC is NO phase at all.8 a5 h2 y9 B- L0 Q9 y, U

' ?+ R, i, S( e' g/ S1 L' ~, bThe only thing you can change the rotation of the motor is the output side of the VFD, NOT the input of the VFD.