[技术互助] A Tip on changing 3 phase AC motor rotation

[复制链接]
鲜花(0) 鸡蛋(0)
发表于 2010-4-14 11:27 | 显示全部楼层 |阅读模式
老杨团队,追求完美;客户至上,服务到位!
本帖最后由 td456 于 2010-4-14 12:28 编辑 ( a% I) G# Y' i1 j3 m

7 H+ g5 f" Y: r, _$ VWe all know that if you want to change the rotation of a three  phase AC motor.
' L0 g+ C9 G; C- b0 E- M* [4 bJust swap any of the two phase leads.
8 ?( D2 `, }0 YBut for VFD application you need to do the swap after the inverter.1 Y! Q- ~! h# K/ N
If you swap the leads before the inverter, it will not work.
鲜花(0) 鸡蛋(0)
发表于 2010-4-14 18:18 | 显示全部楼层
go go go
鲜花(0) 鸡蛋(0)
发表于 2010-4-19 14:38 | 显示全部楼层
Yes, Good point.
! V5 Q% m9 ]( P* l1 z  s  [2 Q4 u0 s- \- p6 @& A; P
As the principal of the VFD works, bascially from AC to DC, then DC to AC. + h) W9 r8 L& b5 F0 g

2 K- f2 \) N1 FThe phase rotation of the output of the VFD connecting to the motor is based on the sequence "open" or "close" controlled by the inverter pre-set inside; any changes to the phase rotation of the feeder will not affect the DC rotation, as DC is NO phase at all.# u  M& m5 v9 c, v6 }

6 q- r0 x2 z3 _; `  ZThe only thing you can change the rotation of the motor is the output side of the VFD, NOT the input of the VFD.