7 A/ r0 f" m* g9 ~3 hTwo cutler –hammer advantage starters are doing the same thing:0 f1 a# p: n: K4 j! C8 K
After start 2-3 times, they will quit working, if you toggle the start and stop buttons on DCS screen , you will get another 2-3 running before they quit working again. 7 ~3 ^$ Q! X/ T9 ]% B1 R
It is a cycle.& F. Y2 E! Y7 u# d- b0 l3 f6 [
# e" b3 j) v, [% S& `+ v, }) \5 yWe isolate the network control and use the local start and stop only, the problem remains.% x& ~/ A' c5 K% o! e
Swap one of the defective buckets with a good one, the new bucket works fine.
2 A6 k9 q/ l* E( R VThe problem should be inside the bucket.% r/ f6 `- \1 L: X6 F# I6 u( ]( Y
3 e9 z+ A7 w9 q8 {5 I0 K1 LWhen the problem happened, we observed that the contactor has a pulling action but will not seal.) X) B# E! |; c9 W9 b& E
Use a terminating screw divers to push in the contactor, it will not seal either.8 [9 A6 A) R# A3 Y' w: N5 j
Confirm with TECH support this should be a problem with the control circuit board inside the advantage starter, we bought two new control circuit boards and replaced the old ones, the problem is still the same.1 D% p3 I+ g& i% o
* B6 s3 P( l& P) P9 n
The next thing we can think of is the coil, we took the coil out to have a close look.
) K6 C8 n; q6 QThey have a fork to pinch inside the two leads to make connection, it is not a good design at all. We soldered the connection and tried again.& P( `5 h, z, r- Q" L1 `' K
It is getting better this time, we have 7-8 times of running before it quit working. ( A: c; E- N4 Z! [. @2 y4 t
) o4 C4 J# U" c7 l2 ^# @
The coil should be the problem, we ordered two of them. But it will take 5-6 weeks for us to get them. & n: K% O5 z( n* a) T, H
7 y( \- V* t* jDo you guys have any input on this issue? |
|