Two cutler –hammer advantage starters are doing the same thing:/ b2 n) v1 R) {$ A
After start 2-3 times, they will quit working, if you toggle the start and stop buttons on DCS screen , you will get another 2-3 running before they quit working again. 8 J7 X9 W$ I7 F J7 g' L& K
It is a cycle.+ w7 j& B8 Z' ?* D/ N* }2 w) m
- H2 R, m+ Y7 UWe isolate the network control and use the local start and stop only, the problem remains.
" H7 x: a* l" U+ v2 Y7 sSwap one of the defective buckets with a good one, the new bucket works fine.
; S% \& a1 I% I3 a+ ~The problem should be inside the bucket.; I$ I4 F: v8 u' d# x
0 r* t9 Q1 V5 ?; IWhen the problem happened, we observed that the contactor has a pulling action but will not seal.
5 a3 d2 s( L" W' CUse a terminating screw divers to push in the contactor, it will not seal either./ @9 h" k# P3 X* @% }: Q# p
Confirm with TECH support this should be a problem with the control circuit board inside the advantage starter, we bought two new control circuit boards and replaced the old ones, the problem is still the same.
3 U8 n2 A- n: I' C: N/ e; c5 W& G" L2 a
The next thing we can think of is the coil, we took the coil out to have a close look.* R, X) c3 Q# h. n5 R5 B5 E
They have a fork to pinch inside the two leads to make connection, it is not a good design at all. We soldered the connection and tried again. R! o' }4 E# v+ A3 y1 s
It is getting better this time, we have 7-8 times of running before it quit working. 1 V+ A0 |3 T% a6 I! v
6 Z- X3 I7 _( v9 ^2 j, [ L4 ~The coil should be the problem, we ordered two of them. But it will take 5-6 weeks for us to get them.
& V4 I* X) k& i B" b4 ]. i& M7 L7 s/ J: y
Do you guys have any input on this issue? |
|