Two cutler –hammer advantage starters are doing the same thing:
, D* M/ v7 W4 H: L After start 2-3 times, they will quit working, if you toggle the start and stop buttons on DCS screen , you will get another 2-3 running before they quit working again. ' x7 u: z K. J% y9 u0 b, o
It is a cycle.3 C' r! p$ M9 b6 O* q8 [/ i
! r, K( r3 m/ i+ E$ {We isolate the network control and use the local start and stop only, the problem remains.
+ c1 r+ |% }# s+ GSwap one of the defective buckets with a good one, the new bucket works fine.
+ M# {$ @* M& N0 GThe problem should be inside the bucket.
: J/ Q6 F0 F) ~$ P; C |) f2 o/ Y" m% ~; Z8 h; Z
When the problem happened, we observed that the contactor has a pulling action but will not seal.3 y, Q- {; |0 n; c! m# c
Use a terminating screw divers to push in the contactor, it will not seal either.7 S+ U0 }9 p1 |1 B* g
Confirm with TECH support this should be a problem with the control circuit board inside the advantage starter, we bought two new control circuit boards and replaced the old ones, the problem is still the same.
, W O* u* b' a: F/ B1 F6 k* B+ B) W
The next thing we can think of is the coil, we took the coil out to have a close look.$ a( `, E, E- a5 u
They have a fork to pinch inside the two leads to make connection, it is not a good design at all. We soldered the connection and tried again.
) |, Q; A1 A- O7 C/ c/ l It is getting better this time, we have 7-8 times of running before it quit working. ; l$ A6 M8 r0 F5 B
% Q7 h9 z# v& _The coil should be the problem, we ordered two of them. But it will take 5-6 weeks for us to get them. : ], t) z! c7 u# u4 e! Y5 Y
: }: O& `9 c8 B( o; `Do you guys have any input on this issue? |
|