[技术互助] A Tip on changing 3 phase AC motor rotation

[复制链接]
鲜花(0) 鸡蛋(0)
发表于 2010-4-14 11:27 | 显示全部楼层 |阅读模式
本帖最后由 td456 于 2010-4-14 12:28 编辑 * X. Y+ C1 T% k( P5 Q$ j7 y3 b9 ~

7 @' _& \4 v2 w: {We all know that if you want to change the rotation of a three  phase AC motor.
# H/ D- f1 N# ~# g+ i8 M) g  w1 qJust swap any of the two phase leads.; C8 _9 ~+ X$ J/ m
But for VFD application you need to do the swap after the inverter.) a2 n, N( k* o
If you swap the leads before the inverter, it will not work.
鲜花(0) 鸡蛋(0)
发表于 2010-4-14 18:18 | 显示全部楼层
go go go
鲜花(0) 鸡蛋(0)
发表于 2010-4-19 14:38 | 显示全部楼层
Yes, Good point.
4 J/ P; V# n3 C4 y+ _
# J" X$ H2 G% l  {6 X2 S& r: |6 cAs the principal of the VFD works, bascially from AC to DC, then DC to AC.
5 w, k: l6 e( t/ g% u) r/ P. D8 L( A1 D5 g* \; X7 G
The phase rotation of the output of the VFD connecting to the motor is based on the sequence "open" or "close" controlled by the inverter pre-set inside; any changes to the phase rotation of the feeder will not affect the DC rotation, as DC is NO phase at all.' s2 s6 G  P9 u2 {# D
7 i8 [( c" L: s! O1 V$ X3 V: l
The only thing you can change the rotation of the motor is the output side of the VFD, NOT the input of the VFD.